that is true if you do NOT network the two Gen3 Wall charger together (1 leaders + upto 5 followers)as initially I had it wired with one 100a breaker in the Hope to load share but the software for The gen 3 wasn’t out yet so I had my electrical guy change it out and split it with 2 50A breakers. So I think the max I can do is 40a each. (80%). Am I thinking of this incorrectly?
your Taycan's maximum L2 charge rate is 48 amps (60 amp breaker)
your wife's Model Y maximum L2 charge rate is 48 amps (60 amp breaker)
48 amp charge rate is 20% faster than 40 amps (8/40 = .20 or 20%)
but if…
- you upgrade the breaker to each Gen3 to 60 amps (along with the wire gauge to each Gen3 EVSE to handle 60/48 amps) - consult your electrician
- minimum wire gauge for 50/40 amp charging circuit is 10 gauge, 8 gauge is better/preferred, 6 gauge is ideal/overkill for 50/40 amps
- 4 gauge wire is recommended for 60 branch circuit - if you have 4 gauge wire already you simply need to swap the breaker - this is easy/peasy
- if you have to pull new wire it may not be worth it…
- but if it's a short and easy run - pulling new wire may not be a big deal.
- configure each Gen3 wall charger to "know" they have a 60 amp breaker (max charge rate for Gen3)
- network/pair/connect them to each other using configuration tool <--- this step is critical - if they don't know they are networked to each other then they each think they have 60 amps (or 120 amps total) - * - see foot note
- now you have a "network/pool" of 2 Gen3 chargers each capable of 60 amps maximum
- as part of the "network" you tell them you are sharing a 100 amp total capacity - this then make them part of a "pool" of chargers - they communicate wirelessly with each other while charging and keep the entire pool of charger under the overall max budget of 100/80 amp - but any single charger can do a maximum of 60/48 amps if there is AMP budget in the pool.
if one vehicle is charging it will get "the full beans" - 60/48 amps of charging
if two vehicles are charging each vehicle will get what it needs…up to a shared combined maximum of 100/80 amps…the two Gen3 chargers will co-operate with each other to intelligently split the charging AMP load as needed but stay under the 100/80 amp overall budget.
the Gen3 wall chargers are actually super awesome - you can have up to
here are the details from Tesla
https://www.tesla.com/support/gen-3-wall-connector-power-sharing
so from picture below
- upgrade the breaker/wire-gauge for each Gen3 wall charger to 60 amps
- connect to one of the Gen3 wall chargers via wifi
- update to the latest firmware
- designate this 1st wall charger the "leader"
- set it's maximum charge rate to 60 amp breaker (48 amp charge rate)
- goto your 2nd wall charger - connect to it's wifi
- update firmware if necessary
- join the 2nd wall charger to the "leader" as a follower
- set the maximum power Sharing settings to 100 amps
- set Powersharing "enabled"
this works great for example if one EV needs 40% capacity charge and the other only need 15%
if they both start charging at the same time (11 pm) they will both share the load of 100/80 amps while charging at the same time (40 amps each) - but when one finishes and drops it's load - the remaining EV will then ramp up to a full 48 amps to finish it's overall charging session faster now that the 1st EV is done…
* - foot note: if you have wire gauge rated for 100 amps to the subpanel - it's probably also rated for 125 amps - consult you're electrician but you can probably just swap the 100 amp breaker for a 125 amp breaker - and then you could just run the two chargers at the full 60/48 amps each since your main breaker is now 125 amps - the issue then would be is the wire for each Gen3 charger rated for 60 amp circuit