I plugged my Taycan in this morning and about an hour later, my wife smelled burning plastic. My NEMA 14-50 receptacle was melting in the garage. It was installed by a trusted electrician but they weren‘t well Experienced in EVs. Btw, the charger has been plugged in for months without being moved. And I have been using this outlet since receiving my 4S in May. 12,000 miles have pulled a lot of kW through this receptacle with no prior problems.

Based on resesrch on other EV forums, certain brands of receptacles have this problem. They seem to be the $8-$15 receptacles that are available at the big box stores. Look up your brand and make sure your outlet is one that an an electrical supply or industrial supplier would sell. Plan to spend $50 or more. I am also replacing my breaker that never tripped and clearing anything combustible from the shelves above my receptacle. And buying another charger supply cable for a cool $115.... But it’s cheaper than a real fire.

Porsche Taycan PSA: Check your charging receptacle 091BDAB0-F129-4E12-8CDE-B9582726AC26


Porsche Taycan PSA: Check your charging receptacle A8A468E0-8793-4344-A655-42B2822E8570
 

chrisk

Well-Known Member
Joined
Dec 3, 2020
Threads
17
Messages
980
Reaction score
1,021
Location
California
Vehicles
2020 Taycan 4S
Country flag
This can happen when the wire nuts that hold the wire in the back get loose. I had one of these cheap receptables that after a few years the nuts would not stay tight and I had it replaced by a new one.
 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
160
Messages
5,810
Reaction score
8,648
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
hubble nema 14-50 industrial/commercial socket - like $80 but you can feel the weight of the unit
 

REIL

Well-Known Member
First Name
Rick
Joined
Dec 8, 2020
Threads
13
Messages
341
Reaction score
304
Location
West US
Vehicles
Taycan 4S+ / MY20
Country flag
I plugged my Taycan in this morning and about an hour later, my wife smelled burning plastic. My NEMA 14-50 receptacle was melting in the garage. It was installed by a trusted electrician but they weren‘t well Experienced in EVs. Btw, the charger has been plugged in for months without being moved. And I have been using this outlet since receiving my 4S in May. 12,000 miles have pulled a lot of kW through this receptacle with no prior problems.

Based on resesrch on other EV forums, certain brands of receptacles have this problem. They seem to be the $8-$15 receptacles that are available at the big box stores. Look up your brand and make sure your outlet is one that an an electrical supply or industrial supplier would sell. Plan to spend $50 or more. I am also replacing my breaker that never tripped and clearing anything combustible from the shelves above my receptacle. And buying another charger supply cable for a cool $115.... But it’s cheaper than a real fire.

091BDAB0-F129-4E12-8CDE-B9582726AC26.jpeg


A8A468E0-8793-4344-A655-42B2822E8570.jpeg
@Td78 Thanks for the heads up. So sorry and glad your wife caught this and limited the damage.
Do you know what your brand of socket was?
 

rquinton

Well-Known Member
First Name
Robert
Joined
Nov 4, 2019
Threads
24
Messages
318
Reaction score
168
Location
Atlanta, GA
Vehicles
Porsche 911, Porsche Taycan 4S (March 2021 arrival date PECATL), 2021 Porsche Cayenne GTS
Country flag


REIL

Well-Known Member
First Name
Rick
Joined
Dec 8, 2020
Threads
13
Messages
341
Reaction score
304
Location
West US
Vehicles
Taycan 4S+ / MY20
Country flag

rquinton

Well-Known Member
First Name
Robert
Joined
Nov 4, 2019
Threads
24
Messages
318
Reaction score
168
Location
Atlanta, GA
Vehicles
Porsche 911, Porsche Taycan 4S (March 2021 arrival date PECATL), 2021 Porsche Cayenne GTS
Country flag
Thanks. Contacted my electrician this morning to change mine to the Hubbell this week after reading Td78's post. Just wanted to know what his was as I suspect I may have the same that burned.
Make sure you are using a 6 gauge wire for 50 amps. Anything higher than that, you are asking for trouble. I agree if your breaker is old from the quote above but that probably wouldn't melt the receptable.
 

REIL

Well-Known Member
First Name
Rick
Joined
Dec 8, 2020
Threads
13
Messages
341
Reaction score
304
Location
West US
Vehicles
Taycan 4S+ / MY20
Country flag
Make sure you are using a 6 gauge wire for 50 amps. Anything higher than that, you are asking for trouble. I agree if your breaker is old from the quote above but that probably wouldn't melt the receptable.
Yes already installed and using for past 3 m months with 6 gauge wire. Bumping up to 60 amp breakers when the electrician installs the Hubbell.
 


rquinton

Well-Known Member
First Name
Robert
Joined
Nov 4, 2019
Threads
24
Messages
318
Reaction score
168
Location
Atlanta, GA
Vehicles
Porsche 911, Porsche Taycan 4S (March 2021 arrival date PECATL), 2021 Porsche Cayenne GTS
Country flag
Yes already installed and using for past 3 m months with 6 gauge wire. Bumping up to 60 amp breakers when the electrician installs the Hubbell.
Check with your electrician but if you have a 50 amp receptacle, you should have a 50 amp breaker. A 60am breaker won't trip if the receptacle has an issue. I am not an electrician but it is rule number 1, match the AMPS to the breaker and the receptacle. There is no value in a 60 amp breaker unless you have a 60 amp receptacle and then your plug won't fit.

BTW, my order is for a Carmine Red 4S+, what interior did you get? I did Black/Limestone
 

REIL

Well-Known Member
First Name
Rick
Joined
Dec 8, 2020
Threads
13
Messages
341
Reaction score
304
Location
West US
Vehicles
Taycan 4S+ / MY20
Country flag
Check with your electrician but if you have a 50 amp receptacle, you should have a 50 amp breaker. A 60am breaker won't trip if the receptacle has an issue. I am not an electrician but it is rule number 1, match the AMPS to the breaker and the receptacle. There is no value in a 60 amp breaker unless you have a 60 amp receptacle and then your plug won't fit.

BTW, my order is for a Carmine Red 4S+, what interior did you get? I did Black/Limestone
Appreciate the comments. My electrician is good and have know him for years, so I trust him and he will do what is required.
Just want to make certain the garage does not burn down.
Congrats on the Carmine Red. You will enjoy it!
I did not spec my vehicle as I got it from my Porsche center with a few hundred miles on it. CPO six year unlimited warranty other goodies added and a very good price.
Image of interior included for you.

Porsche Taycan PSA: Check your charging receptacle 8EFE7E02-E25E-4F12-A6A7-00268C0F4F78


Porsche Taycan PSA: Check your charging receptacle 28914E7D-AA95-4E2E-BBB1-C4050C4457EB
 
Last edited:

chrisk

Well-Known Member
Joined
Dec 3, 2020
Threads
17
Messages
980
Reaction score
1,021
Location
California
Vehicles
2020 Taycan 4S
Country flag
Make sure your electricians torque the screws that hold the wires to spec. Every 14-50 receptacle has a torque spec for its screws and electrician rarely follow it. If your electrician does not have a torque screw driver then you know he is not up to the task.
 

rquinton

Well-Known Member
First Name
Robert
Joined
Nov 4, 2019
Threads
24
Messages
318
Reaction score
168
Location
Atlanta, GA
Vehicles
Porsche 911, Porsche Taycan 4S (March 2021 arrival date PECATL), 2021 Porsche Cayenne GTS
Country flag
Appreciate the comments. My electrician is good and have know him for years, so I trust him and he will do what is required.
Just want to make certain the garage does not burn down.
Congrats on the Carmine Red. You will enjoy it!
I did not spec my vehicle as I got it from my Porsche center with a few hundred miles on it. CPO six year unlimited warranty other goodies added and a very good price.
Image of interior included for you.

8EFE7E02-E25E-4F12-A6A7-00268C0F4F78.jpeg


28914E7D-AA95-4E2E-BBB1-C4050C4457EB.jpeg
Did you get the passenger screen (hard to tell) and if so, what do you think of it? Can you run a separate phone to it so you can drive and have your calls on the main PCM and your passenger have their phone hooked to the other screen? Does Carplay work on the passenger screen from the linked phone? There is very little on what the passenger screen actually does. I ordered as a party trick but I hope it is somewhat useful.
 
OP
OP
Td78

Td78

Well-Known Member
Joined
Dec 27, 2019
Threads
11
Messages
135
Reaction score
194
Location
Colorado
Vehicles
Taycan 4S
Country flag
@Td78 Thanks for the heads up. So sorry and glad your wife caught this and limited the damage.
Do you know what your brand of socket was?
@REIL Thank you. It was Leviton brand. This happened to be the same brand with which many others on T forums had nearly identical problems. I heard good things about the Hubbell brand. And Cooper too. Thanks all for the advice.
 

REIL

Well-Known Member
First Name
Rick
Joined
Dec 8, 2020
Threads
13
Messages
341
Reaction score
304
Location
West US
Vehicles
Taycan 4S+ / MY20
Country flag
@REIL Thank you. It was Leviton brand. This happened to be the same brand with which many others on T forums had nearly identical problems. I heard good things about the Hubbell brand. And Cooper too. Thanks all for the advice.
Thank you. Mine is Leviton. It will be changed to the Hubbell this week. Your PSA is greatly appreciated.