Breaker Tripping When Charging
eisenb11
Redondo Beach, CA
Taycan RWD
I’ll differ to you on this. Mine is not an AFCI Breaker
I don't get what you're saying. Are you saying that you're not on an AFCI breaker and are NOT having problems? Or you are on a non-AFCI breaker and you ARE having problems?
If you are on a non-AFCI breaker and you ARE having problems, then I stand by what I've said that something seems to be wrong as you shouldn't be popping that 50A breaker.
- Edit - Found your earlier post:
" I’ve had the same issue with both a juice box and Enel - turned down max charge from 40 to 38 and problem went away"
That shouldn't be required - makes me think something is either wrong with the charger or with the breaker if a small 2A change fixes the problem, no?
RPSRPS
Richard
New Jersey / Vermont
'22 TAYCAN GTS / '25 RIVIAN RIT TRI / '19 RANGER
I’m not having the issue, I was relaying my experience to the gentleman who was. My problem was reconciled by lowering the charging amperage to 38 from 40. I had just mentioned to him that I thought my issue might have also had something to do with the draw from when my AC came on.
eisenb11
Redondo Beach, CA
Taycan RWD
Yeah, I found your earlier post after I posted that. I'm thinking that what you're doing is more of a workaround, though, as perhaps addressing the root cause of the issue.
In general, that breaker shouldn't be popping under normal conditions (which does include a car charging starting up or an A/C in your case). I'm more inclined to place the blame on faulty equipment - either the breaker or the device consuming the electricity is malfunctioning and drawing more than it should or some other issue.
NetArchitect
DallasTX
2024 Taycan 4S
Just to give an update.. Emporia replaced my evse and I was able to use it fine with my Taycan. However when I try to charged it using my ID.4 thats when the breaker trip again. So it doesn’t seem like a Taycan issu anymore. Right now I just don't charge my id.4 anymore at home. I will probably have someone build another breaker for ithe id.4? I did send it to the dealer and it charged correctly with their L2 evse
If breaker trips when ID.4 charges, there is something wrong with ID.4 - probably its on-board charging system. Need to have its on-board charging system checked. Just because it charged correctly at dealer does not mean it is working properly.
Try charging the ID.4 at a public AC charger.
David Bennett
Taycan 4S, Golf 8r
I’ve had the same issue with both a juice box and Enel - turned down max charge from 40 to 38 and problem went away. I also had issue during A/C season, the spike in draw when A/C came on would trip my breaker
Do you know what class of breaker you have? Your A/C compressor might have a high inrush current and require a class 30 to prevent nuisance tripping.
BayouTiger
Chuck
Mid Tennessee
23 Taycan GTS, Ford F250, Jeep Trackhawk
So I did some digging - are you sure you have a NEMA 15-40??? I’m thinking that you have a NEMA 14-50.
If you have a 14-50 on a 50A breaker (like I do) then 40A charging is technically correct.
Note: one other poster suggested 38A.
A 40A charger would go on a 50A circuit with the 14-50R receptacle due to the 80% rule for circuit loading. A 40A circuit would limit you to 32A@240 (7.68kw). At least for the US.