I wasn’t home to look it up earlier, but it’s NEC 210.21(B)1 for the code cite on the OCPD rating for single receptacle branch circuits.

Depending on how far away your receptacle is from your panel, you may want to consider running a larger 100A or more feed to a subpanel closer to your destination and then branching the 50A breaker and receptacle off of that. That’s what I did with a 125A sub panel in my garage with EVSE circuits off of that. Then you have more options for easier future expansion if you add additional electric vehicles.
I went the 100AMP subpanel route as well. It is one of the most costly options but I went this route mostly for the purposes of easily supporting 2 EVs in the future. The 11KW vs 9.6KW upgrade isnt a bad idea if you only ever plan on supporting one vehicle.

Note: the some chargers that can work together to share a single circuit…so that is something to consider if you are ok with slower charging for two vehicles in future as well.
Sponsored

 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
193
Messages
7,025
Reaction score
10,509
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
Note: the some chargers that can work together to share a single circuit…so that is something to consider if you are ok with slower charging for two vehicles in future as well.
multiple chargers sharing a single circuit is a really really really excellent solution (ClipperCreek share2 feature) - sharing a 60/80/100 amp circuit is fantastic for charging multiple EV's and in practice works really well because rarely do both EV's need a full-battery-capacity charge from daily use…so the fact that when charging 2 is "slower" doesn't matter - cause both will still be ready well before you wake up in the morning

on the rare days you do have a "full" deep charge - you plug only one vehicle in and that single EV will get "full capacity" charging speed cause the dynamic sharing of the single breaker will give full breaker capacity (20% rule still in effect) to the single EV charging…

shared EV chargers on a single breaker is a fantastic and nearly future-proof approach for the eventually multi-EV household.
 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
193
Messages
7,025
Reaction score
10,509
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
this is the simplest way to support Two EV's

https://store.clippercreek.com/level2/level2-40-to-80/40-amp-dual-evse-6-50

NEMA 6-50 plug - and has two cords for 9.6 kW charging - supports charing one or two EV's at the same time…no new circuit required - and 14-50 to 6-50 plug swap is _TRIVIAL_ easy…

honestly the best/simpliest and affordable multi-EV upgrade from a EV charging company with an excellent reputation.

Porsche Taycan NEMA 14-50 outlet question D3EBA22B-020C-4984-9A8D-F1F56E21F3FB
 

Jhenson29

Well-Known Member
First Name
Jeremy
Joined
Feb 9, 2021
Threads
37
Messages
3,015
Reaction score
4,651
Location
St. Louis, MO
Vehicles
2022 Macan S; 2021 Taycan 4S
Country flag
I went the 100AMP subpanel route as well.
I really think something along those lines should be getting considered by everyone doing this as we’re only going to get more and not less EVs.

Unfortunately, the cost may put people off, especially if they’re already buying a new car.

And some people’s situations may not warrant it for themselves. They may live alone and only have one vehicle or they may be selling their house in the near future and won’t be able to recup the costs or 10 other reasons I can’t think of because I’m not in those situations.

I do think larger EVSE capacity will be a selling point in the housing market in the future. Maybe 10 years, just to put a ballpark number to it. It’s going to be like an extra bedroom or bathroom once it’s common for families to have multiple EVs. Just thinking out loud.
 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
193
Messages
7,025
Reaction score
10,509
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
NEMA 14-50/6-50 is fine for 99.999999% of daily driving scenarios and even fine for the rare case you come home at 3% SOC and need to charge back to 85%…

NEMA 14-50 is just fine…
 


RAHRCR

Well-Known Member
Joined
Jan 19, 2022
Threads
46
Messages
1,860
Reaction score
2,054
Location
Northeast, US
Vehicles
Taycan Cross Turismo 4S
Country flag
I really think something along those lines should be getting considered by everyone doing this as we’re only going to get more and not less EVs.

Unfortunately, the cost may put people off, especially if they’re already buying a new car.

And some people’s situations may not warrant it for themselves. They may live alone and only have one vehicle or they may be selling their house in the near future and won’t be able to recup the costs or 10 other reasons I can’t think of because I’m not in those situations.

I do think larger EVSE capacity will be a selling point in the housing market in the future. Maybe 10 years, just to put a ballpark number to it. It’s going to be like an extra bedroom or bathroom once it’s common for families to have multiple EVs. Just thinking out loud.
Agreed. I believe there will become a point where cars with 400-500 miles of range will be considered “average” and having the increased charging capacity to support them will make a home more attractive.
 

Allegedly

Well-Known Member
Joined
Mar 17, 2022
Threads
0
Messages
51
Reaction score
71
Location
US
Vehicles
'22 Land Rover Defender, '22 Ford Bronco, '22 Tayc
Country flag
I have 60A fuse setup with 60A rated 6 AWG wire on a hard wired ChargePoint Homeflex charger and consistently get 10.5A to the car (11A at charger) and without any doubt shave a couple of hours minimum off full charging times - super happy that I went that route for essentially no extra cost as was initially planning identical wire setup for a 40A setup plug in with a 50A fuse. Have an additional 40-50 Nema plug in adjacent bay for the future Mini electric :). I went for the hard wire as of course have the Porsche portable charger and obviously was never planning on moving the ChargePoint.
Same exact setup. Love the ChargePoint. I was lucky enough to have the service entrance on the back side of this garage wall so 5 ft of #6 on a 60A worked great. Installed it myself. Super easy.

Porsche Taycan NEMA 14-50 outlet question PXL_20220428_115648588
 

daveo4EV

Well-Known Member
First Name
David
Joined
Jan 28, 2019
Threads
193
Messages
7,025
Reaction score
10,509
Location
Santa Cruz
Vehicles
Cayenne Hybrid, 911(s) GT3/Convertable
Country flag
for me owning EV's since 2012 (Ford Focus EV was my first) - the ONLY time charging speed matters is when I'm trying to turn the vehicle around and have a "schedule" - i.e. I'm only going to be home for like 2 or 3 hours and want to pump as many electrons into the battery as possible…

in practice this happens to me personally 3-4 days a year - the other 360 days a year charging time does not matter…

the days it does happen are when I'm behaving more like an uber than a daily driver - mostly airport shuttle days when I'm shuttling in-laws to/from the airport on different arrival/departure schedules or different airports (SFO/SJC/OAK)

however what has happened since 2012 is the rise of fast charging - and honestly 10-20 min stop at any of these fast chargers (even the 50 kW ones) will do more charging than the most expensive 100 amp home charging setup ever will…

the _OTHER_ reason to have faster charging at home is for when you forget to plug in - and realize at 4 am that you need to leave for work at 7 am - and oh sh*t I need to rush to the garage and plug in so I get as much capacity as possible before I get on the road…

99% of the time charging time does not matter cause it will be done in 3 hours or less which means the car is "full" 6 hours before I wake up in the morning…

the rise of fast charging as a "thing" means home charging and high capacity home charging is less critical than it was 4 years ago - see map below - all the orange "pins" are fast chargers you can use in case you home setup fails to meet your needs 0.01% of the time

and fast charging is going to be more fast charging sites in the future - not fewer…

perhaps the money you can save on a smaller home charging setup can be use to add the $460 400V/150 kW charging option - :cool::rock::p

Porsche Taycan NEMA 14-50 outlet question E6ECF02E-0193-4337-A4AD-D683402EE43E
 


Wakesurfer

Well-Known Member
First Name
Bob
Joined
Nov 19, 2020
Threads
4
Messages
245
Reaction score
307
Location
Granbury, Texas
Vehicles
2021 Taycan 4S, 2023 YukonXL, 2024 Macan S
Country flag
Darn my electrician already bought the #6 wire, so according to that chart if I ever want to have a 60 amp breaker I'll need it rewired.
I used 6 gauge as well assuming that we would have just one charger. Same position as you - IF we add another EV and add another charger we will need to go to a heavier gauge, etc. But my outlet is only about 20 feet from the electrical box in the garage and easily accessible so it will be a minor project to re-do. If we add another EV we just might try living with charging one car at a time and see how that works out. We are both retired so charging both cars at the same time is not imperative if it every comes down to that.
 

Jhenson29

Well-Known Member
First Name
Jeremy
Joined
Feb 9, 2021
Threads
37
Messages
3,015
Reaction score
4,651
Location
St. Louis, MO
Vehicles
2022 Macan S; 2021 Taycan 4S
Country flag
the _OTHER_ reason to have faster charging at home is for when you forget to plug in - and realize at 4 am that you need to leave for work at 7 am - and oh sh*t I need to rush to the garage and plug in so I get as much capacity as possible before I get on the road…
Lol…that’s me….glad I got the 19.2….?
 

RAHRCR

Well-Known Member
Joined
Jan 19, 2022
Threads
46
Messages
1,860
Reaction score
2,054
Location
Northeast, US
Vehicles
Taycan Cross Turismo 4S
Country flag
for me owning EV's since 2012 (Ford Focus EV was my first) - the ONLY time charging speed matters is when I'm trying to turn the vehicle around and have a "schedule" - i.e. I'm only going to be home for like 2 or 3 hours and want to pump as many electrons into the battery as possible…

in practice this happens to me personally 3-4 days a year - the other 360 days a year charging time does not matter…

the days it does happen are when I'm behaving more like an uber than a daily driver - mostly airport shuttle days when I'm shuttling in-laws to/from the airport on different arrival/departure schedules or different airports (SFO/SJC/OAK)

however what has happened since 2012 is the rise of fast charging - and honestly 10-20 min stop at any of these fast chargers (even the 50 kW ones) will do more charging than the most expensive 100 amp home charging setup ever will…

the _OTHER_ reason to have faster charging at home is for when you forget to plug in - and realize at 4 am that you need to leave for work at 7 am - and oh sh*t I need to rush to the garage and plug in so I get as much capacity as possible before I get on the road…

99% of the time charging time does not matter cause it will be done in 3 hours or less which means the car is "full" 6 hours before I wake up in the morning…

the rise of fast charging as a "thing" means home charging and high capacity home charging is less critical than it was 4 years ago - see map below - all the orange "pins" are fast chargers you can use in case you home setup fails to meet your needs 0.01% of the time

and fast charging is going to be more fast charging sites in the future - not fewer…

perhaps the money you can save on a smaller home charging setup can be use to add the $460 400V/150 kW charging option - :cool::rock::p

E6ECF02E-0193-4337-A4AD-D683402EE43E.jpeg
Generally agree with the rationale here. For me, if I am charging outside of my home, this is an indication that something went horribly wrong that day. I am unlikely to use an EV for extended travel until I am driving a Gen 2 Porsche EV.
 

nickmdp

Well-Known Member
Joined
Nov 18, 2021
Threads
3
Messages
325
Reaction score
555
Location
Midwest
Vehicles
2022 Taycan GTS ST
Country flag
this is the simplest way to support Two EV's

https://store.clippercreek.com/level2/level2-40-to-80/40-amp-dual-evse-6-50

NEMA 6-50 plug - and has two cords for 9.6 kW charging - supports charing one or two EV's at the same time…no new circuit required - and 14-50 to 6-50 plug swap is _TRIVIAL_ easy…

honestly the best/simpliest and affordable multi-EV upgrade from a EV charging company with an excellent reputation.
I have that exact charger and can vouch for it being a great fit for us. The one thing to triple check is the distance to both car locations and their charging ports, as the 25' reach sounds great but can be shorter than you'd think. The EVSE is great though, and haven't had a problem with it yet.
 

ciaranob

Well-Known Member
Joined
Jul 3, 2021
Threads
83
Messages
3,547
Reaction score
2,639
Location
Houston, TX
Vehicles
CT4S 2022 Mini Cooper S 2024 Electric in 2025/6
Country flag
Same exact setup. Love the ChargePoint. I was lucky enough to have the service entrance on the back side of this garage wall so 5 ft of #6 on a 60A worked great. Installed it myself. Super easy.
Ditto in that my main 100A garage supply is literally behind the wall mounting just offset a few more feet than yours :)

Excellent charger highly rated when you search reviews and 100% effective - WiFi access too has been flawless too since installed 6 months ago.

Porsche Taycan NEMA 14-50 outlet question IMG_7443.JPG
 
OP
OP
IrwinJ

IrwinJ

Well-Known Member
First Name
Irwin
Joined
Apr 17, 2022
Threads
43
Messages
197
Reaction score
71
Location
Asheville NC
Vehicles
Mercedes SL550
Country flag
Ditto in that my main 100A garage supply is literally behind the wall mounting just offset a few more feet than yours :)

Excellent charger highly rated when you search reviews and 100% effective - WiFi access too has been flawless too since installed 6 months ago.

IMG_7443.JPG
just curious, what is benefit/reason you're using a third party charger as opposed to the charger that comes with the car?
 

ciaranob

Well-Known Member
Joined
Jul 3, 2021
Threads
83
Messages
3,547
Reaction score
2,639
Location
Houston, TX
Vehicles
CT4S 2022 Mini Cooper S 2024 Electric in 2025/6
Country flag
just curious, what is benefit/reason you're using a third party charger as opposed to the charger that comes with the car?
Numerous discussions on this in Forum - no real benefit at all if all you need is the std 40A plug in wall charger. However, as I previously stated, I have a hard wired 50A (60A fuse) setup for my ChargePoint with faster charging to my car which I prefer.

Also I will never forget to bring my portable as it lives 100% of the time in my car :) - have done multiple long trips using destination chargers and/or B&B supplied 14-50 sockets where I use the portable charger. So mostly just convenience for me and a realized boost in charge rate at home with the hard wired setup.
Sponsored

 
 